Questions # 11:

You are allowed to use a calculator for this question. The total power consumption of the ICT equipment in a rack is 6 kW. The equipment is traditional ICT equipment with a Delta-T of approximately 11 °C / 20 °F. Calculate the approximate CFM required to cool the equipment in the rack.

Options:

A.

Approximately 1,500 CFM


B.

Approximately 1,000 CFM


C.

Approximately 500 CFM


D.

Approximately 160 CFM


Expert Solution
Questions # 12:

You want to manage temperature and humidity only at the facility level in your data center. All servers use front-to-rear airflow. Which location for measurement should you recommend?

Options:

A.

At the back/rear of the server at 50 mm (2 in)


B.

At 1.5 m (5 ft) above the floor, 0.4 m (15 in) in front of the rack


C.

At the front/intake of the server at 50 mm (2 in)


D.

At 1.5 m (5 ft) above the floor, 0.4 m (15 in) at the back of the rack


Expert Solution
Questions # 13:

Racks with 1.0 m depth and cold aisle containment with 3 perforated tiles are used. What aisle pitch is recommended?

Options:

A.

5 tiles pitch rule


B.

7 tiles pitch rule


C.

8 tiles pitch rule


D.

10 tiles pitch rule


Expert Solution
Questions # 14:

Which class of UPS is ideal for data centers?

Options:

A.

VFD (Voltage and Frequency Dependent)


B.

VI (Voltage Independent)


C.

VFI (Voltage and Frequency Independent)


D.

First class


Expert Solution
Questions # 15:

Do you need to consider bullet (ballistic) protection when designing a data center?

Options:

A.

No; bullet protection is not a requirement of ANSI/TIA-942


B.

No, there is no reason for implementing bullet protection as you cannot predict the type of weapons that might be used


C.

Yes, but only when the data center is built in an area with a high criminality rate or with a risk of terrorist attacks


D.

Yes, bullet protection is a requirement of ANSI/TIA-942 for Rated-3/4 data centers


Expert Solution
Questions # 16:

What mainly affects the cooling capacity of a raised floor tile?

Options:

A.

Type of ICT equipment, location of the air conditioner, pressure under the raised floor, allowable temperature in the hot aisle


B.

Relative humidity in the computer room, temperature of the cold air, pressure under the raised floor, construction material of the tile


C.

Percentage of the surface opening, obstruction of the supporting construction, pressure under the raised floor, damper construction


D.

Percentage of the surface opening, airflow direction of the ICT equipment, temperature difference between the air intake and air exhaust of the ICT equipment, construction material of the tile


Expert Solution
Questions # 17:

The data center has been in operation for about 1 year and 2 months. The dust levels in the computer room are relatively high.

What is the most likely root cause?

Options:

A.

The cleaning crew is not doing their work properly


B.

Every computer room has high dust levels due to constant high-speed air movement


C.

Low pressure in the computer room


D.

Floorboards are most likely not fitted correctly


Expert Solution
Questions # 18:

Can you install a raised floor tight to the perimeter of the room?

Options:

A.

Yes, but only if the data center is located in Zone 0 with no or little seismic activity


B.

Yes, a raised floor needs to be installed tight to the perimeter to prevent air leakage


C.

No, to avoid damage to the raised floor due to building and hygrothermal movement


D.

No, but this applies only to raised floors with a height of over 90 cm (3 ft)


Expert Solution
Questions # 19:

Management has requested a 15-minute battery bank assuming full load on the UPS. The UPS vendor has provided the following specifications of the UPS:

•Rated power: 30 kVA

•Rectifier input voltage: 400 V/3 phase

•Rectifier input power factor: 0.8

•Battery rated voltage: 384 V

•Number of cells: 192

•End of discharge voltage: 308 V

•Inverter output voltage: 400 V/3 phase

•Inverter output power factor: 0.8

What information is missing to perform the battery calculation?

Options:

A.

UPS efficiency


B.

Inverter efficiency


C.

Load imbalance on the phases


D.

Available battery charging current


Expert Solution
Questions # 20:

Given: A = attenuation in dB, R = real measured value, M = maximum acceptable value. Which formula should be used to calculate the required attenuation factor of EMF shielding material?

Options:

A.

A = 10 log (R/M)


B.

A = 20 log (M/R)


C.

A = 10 log (M/R)


D.

A = 20 log (R/M)


Expert Solution