You are allowed to use a calculator for this question. The total power consumption of the ICT equipment in a rack is 6 kW. The equipment is traditional ICT equipment with a Delta-T of approximately 11 °C / 20 °F. Calculate the approximate CFM required to cool the equipment in the rack.
You want to manage temperature and humidity only at the facility level in your data center. All servers use front-to-rear airflow. Which location for measurement should you recommend?
Racks with 1.0 m depth and cold aisle containment with 3 perforated tiles are used. What aisle pitch is recommended?
Which class of UPS is ideal for data centers?
Do you need to consider bullet (ballistic) protection when designing a data center?
What mainly affects the cooling capacity of a raised floor tile?
The data center has been in operation for about 1 year and 2 months. The dust levels in the computer room are relatively high.
What is the most likely root cause?
Can you install a raised floor tight to the perimeter of the room?
Management has requested a 15-minute battery bank assuming full load on the UPS. The UPS vendor has provided the following specifications of the UPS:
•Rated power: 30 kVA
•Rectifier input voltage: 400 V/3 phase
•Rectifier input power factor: 0.8
•Battery rated voltage: 384 V
•Number of cells: 192
•End of discharge voltage: 308 V
•Inverter output voltage: 400 V/3 phase
•Inverter output power factor: 0.8
What information is missing to perform the battery calculation?
Given: A = attenuation in dB, R = real measured value, M = maximum acceptable value. Which formula should be used to calculate the required attenuation factor of EMF shielding material?