Exin EXIN EPI Certified Data Centre Specialist CDCS Question # 19 Topic 2 Discussion

Exin EXIN EPI Certified Data Centre Specialist CDCS Question # 19 Topic 2 Discussion

CDCS Exam Topic 2 Question 19 Discussion:
Question #: 19
Topic #: 2

Management has requested a 15-minute battery bank assuming full load on the UPS. The UPS vendor has provided the following specifications of the UPS:

•Rated power: 30 kVA

•Rectifier input voltage: 400 V/3 phase

•Rectifier input power factor: 0.8

•Battery rated voltage: 384 V

•Number of cells: 192

•End of discharge voltage: 308 V

•Inverter output voltage: 400 V/3 phase

•Inverter output power factor: 0.8

What information is missing to perform the battery calculation?


A.

UPS efficiency


B.

Inverter efficiency


C.

Load imbalance on the phases


D.

Available battery charging current