Questions # 21:

When commissioning a PV system, which test is most critical to verify proper operation of the array before connecting to the inverter?

Options:

A.

Insulation resistance test


B.

Open-circuit voltage test


C.

Short-circuit current test


D.

Ground-fault detection test


Expert Solution
Questions # 22:

A ground-mount array uses driven piles with a lateral load capacity of 500 lbs. The wind load calculation yields a lateral force of 600 lbs per pile. What must be done?

Options:

A.

Increase pile depth


B.

Add additional piles


C.

Use a different foundation type


D.

Any of the above


Expert Solution
Questions # 23:

A PV system’s capacity factor is 18%. The array is 10 kW, and it operates 365 days/year. What is the annual energy output?

Options:

A.

12,264 kWh


B.

15,768 kWh


C.

18,000 kWh


D.

21,024 kWh


Expert Solution
Questions # 24:

A module’s power is 340W at STC. At 700 W/m² and 40°C with a coefficient of -0.38%/°C, what is the output?

Options:

A.

224W


B.

236W


C.

248W


D.

260W


Expert Solution
Questions # 25:

A 20 kW system has a measured output of 18 kW at STC. What is the total system loss?

Options:

A.

5%


B.

10%


C.

15%


D.

20%


Expert Solution
Questions # 26:

Which of the following is an NEC requirement regarding access for large-scale PV electric power production facilities?

Options:

A.

Field-applied hazard markings must be installed, and access to the supply station is to be restricted by fencing or other adequate means.


B.

All fencing and associated gates must have ac and dc current and voltage exposure labvels and must be electrically isolated from the solar facility.


C.

Arc flash warning labels must be field-applied by the installer at all access points for qualified persons and at the point of the utility interconnection directory.


D.

Access to remote isolating equipment for servicing is allowed for individual other than qualified persons when the equipment is enclosed within a secure structure.


Expert Solution
Questions # 27:

An installer is working on a 1000V DC PV array. What is the minimum PPE required per NFPA 70E for arc flash protection?

Options:

A.

Category 1 PPE


B.

Category 2 PPE


C.

Category 3 PPE


D.

Category 4 PPE


Expert Solution
Questions # 28:

A PV system uses 10 AWG USE-2 wire for a 150-foot source circuit run with an Isc of 8A. The terminals are rated at 75°C. What is the ampacity of the conductor after applying NEC temperature and conduit fill adjustments at 35°C?

Options:

A.

30A


B.

35A


C.

40A


D.

45A


Expert Solution
Questions # 29:

A PV system equipped with rapid shutdown requires a label stating ‘’RAPID SHUTDOWN SWITCH FOR SOLAR PV SYSTEM’’.

Which is the BEST description of where this label is required?

Options:

A.

On or within 3 ft. of the ac disconnect


B.

On or within 3 ft. of the ac disconnect


C.

On or within 3 ft. of the ac disconnect


D.

On or within 3 ft. of the ac disconnect


Expert Solution
Questions # 30:

A 1. 100 ft, 2 ranch home with cathedral callings has a 14 ft. x 41 ft. 8 in , south-facing , composite shingle roof. An engineer has determined that the home’s 2 in, x 6 in. on-center roof rafters are strong enough to gold a solar electric system. The system will have 62.25 in. x 32.50 in. modules with a 1-in gap between modules and a standard twin-rill mounting system number of modules that can fit on the roof on under these conditions?

Options:

A.

28 modules in portrait


B.

30 modules in portrait


C.

35 modules in landscape


D.

40 modules in landscape


Expert Solution
Viewing page 3 out of 5 pages
Viewing questions 21-30 out of questions