The duration of required fire flow in public supply systems depends on the type of occupancy, construction, and exposure of the building, as well as the availability and reliability of the water supply. According to NFPA 1, Fire Code, Table 18.4.5.1.2, the minimum duration of fire flow for most occupancies ranges from 1 to 4 hours, with some exceptions for high-rise buildings, health care facilities, and special hazards. The fire flow duration is intended to provide enough water for fire suppression and exposure protection until the fire is under control or extinguished.References: NFPA 1, Fire Code, 2023 Edition, Section 18.4.5.1.2 and Table 18.4.5.1.2; NFPA Fire Protection Handbook, 21st Edition, Chapter 9, Section 9.2.2.