PVIP Exam Topic 3 Question 20 Discussion:
Question #: 20
Topic #: 3

A PV technician is installing a 6.5KWac inverter using a 40A backfed breaker. The single line shows a 200A panelboard with a 200A breaker, but the installer finds that the panelbord actually has a 150A main breaker. Which of the following is the CORRECT installation option?


A.

Replace the 200A panel with a 150A panel.


B.

Install a 30A backfed circuit breaker.


C.

Change the main circuit breaker to a 200A unit.


D.

Complete the installation as noted above.