Questions # 11:

A fire pump must produce at least what percentage of its rated pressure at the 150% flow condition?

Options:

A.

50%


B.

65%


C.

100%


D.

120%


Expert Solution
Questions # 12:

A warehouse has palletized storage of empty wood crates on wood pallets to a height of 11 ft (3.4 m). What is the

minimum design density?

Options:

A.

0.15 gpm/ft2 (6.1 mm/min)


B.

0.20 gpm/ft2 (8.1 mm/min)


C.

0.23 gpm/ft2 (9.2 mm/min)


D.

0.25 gpm/ft2 (10.2 mm/min)


Expert Solution
Questions # 13:

The purpose of the owner's certificate is to

Options:

A.

help ensure that the capability of the sprinkler system is adequate to address the hazard.


B.

replace project plans.


C.

obtain the building permit.


D.

be a declaration by the sprinkler contractor as to the hazards in the building.


Expert Solution
Questions # 14:

In a dry pipe system protection of an Extra Hazard Group I occupancy, how many remote sprinklers should be

considered to initially open to meet the water delivery time requirements?

Options:

A.

1


B.

2


C.

3


D.

4


Expert Solution
Questions # 15:

High piled storage includes all storage of Group A plastic in excess of what height?

Options:

A.

5 ft (1.5 m)


B.

6 ft (1.8 m)


C.

8 ft (2.4 m)


D.

12 ft (3.7 m)


Expert Solution
Questions # 16:

Working plans are required to have the total system volume of the system for

Options:

A.

wet systems.


B.

open-head deluge systems.


C.

dry systems.


D.

antifreeze systems.


Expert Solution
Questions # 17:

When utilizing ordinary temperature CMDA sprinkler protection for a single-row rack storage of an unencapsulated Class I commodity stored 15 ft (4.6 m) high without in-rack sprinklers with 8 ft (2.4 m) aisles, what is the minimum design density required?

Options:

A.

0.20 gpm/ft2 (8.1 mm/min)


B.

0.32 gpm/ft2 (13 mm/min)


C.

0.54 gpm/ft2 (22 mm/min)


D.

0.86 gpm/ft2 (35 mm/min)


Expert Solution
Questions # 18:

For an Extra Hazard Group 1 remote area of 2,500 ft2 (232.25 m2) using fire sprinklers with a coverage area of

92 ft2 (8.547 m2), how many gallons per minute of water are required per sprinkler?

Options:

A.

23.0 gpm (87.055 lpm)


B.

26.8 gpm (101.449 lpm)


C.

31.3 gpm (118.394 lpm)


D.

36.8 gpm (139.288 lpm)


Expert Solution
Questions # 19:

When backflow prevention valves are installed on existing pipe scheduled systems, the friction losses of the device shall be accounted for when determining

Options:

A.

residual pressure.


B.

system flow requirements.


C.

static pressure.


D.

system GPM requirements.


Expert Solution
Questions # 20:

A new office area located inside a warehouse space is being designed as a light hazard occupancy. This office area

may be protected with

Options:

A.

quick-response CMSA sprinklers.


B.

standard-response CMSA sprinklers.


C.

standard-response spray sprinklers.


D.

residential sprinklers.


Expert Solution