Questions # 31:

The point-of-utility connection of a residential utility-interactive PV system is in the main distribution panel. If the busbars of the main distribution panel are rated at 200A, and if the distribution panel has a 200A main breaker, the rated output current of the inverter cannot exceed.

Options:

A.

24A


B.

32A


C.

40A


D.

200A


Expert Solution
Questions # 32:

What is the maximum allowable voltage drop for a PV source circuit conductor run of 100 feet, using 10 AWG copper wire, if the system operates at 48V DC and the design specifies a 2% voltage drop?

Options:

A.

0.48V


B.

0.96V


C.

1.44V


D.

1.92V


Expert Solution
Questions # 33:

During a site assessment, an installer identifies a 100-foot-tall tree 150 feet south of a proposed PVarray. The site latitude is 40°N. Will this tree cause shading on December 21st between 9 AM and 3 PM solar time?

Options:

A.

Yes, shading will occur all day


B.

Yes, shading will occur before 10 AM only


C.

No, shading will not occur


D.

Insufficient data to determine


Expert Solution
Questions # 34:

Which insulation color is allowed for a current-carrying root top dc conductor on a functionally grounded 6kw PV system?

Options:

A.

Red


B.

White


C.

Green


D.

Green/yellow


Expert Solution
Questions # 35:

A PV array produces 10 kW at 25°C. At 50°C with a coefficient of -0.45%/°C, what is the output?

Options:

A.

8.9 kW


B.

9.1 kW


C.

9.3 kW


D.

9.5 kW


Expert Solution
Questions # 36:

A 5 kW PV system has a derate factor of 0.82. The site receives 5.5 PSH daily. What is the expected daily AC energy output?

Options:

A.

20.5 kWh


B.

22.55 kWh


C.

25.0 kWh


D.

27.5 kWh


Expert Solution
Questions # 37:

A bifacial PV module has a rated power of 350W on the front side and a bifaciality factor of 70%. If the rear side receives 200 W/m² of irradiance, what is the total power output under STC front-side conditions (1000 W/m²)?

Options:

A.

385W


B.

420W


C.

449W


D.

490W


Expert Solution
Questions # 38:

During a PV system inspection, an installer notices that the rapid shutdown system fails to de-energize the array within 30 seconds of initiation. What is the most likely cause based on NEC 690.12 requirements?

Options:

A.

The rapid shutdown switch is installed more than 10 feet from the array


B.

The system lacks a compatible rapid shutdown device


C.

The inverter is not listed for rapid shutdown compliance


D.

The array conductors exceed the maximum allowable voltage


Expert Solution
Questions # 39:

A PV system has a nameplate capacity of 10 kW DC and operates with a total system derate factor of 0.85. What is the expected AC output power under standard test conditions (STC)?

Options:

A.

7.5 kW


B.

8.5 kW


C.

9.0 kW


D.

10.0 kW


Expert Solution
Questions # 40:

A 15 kW system has a total derate factor of 0.90. After 5 years, output drops by 2% annually due to degradation. What is the AC output in year 5?

Options:

A.

11.5 kW


B.

12.2 kW


C.

12.9 kW


D.

13.5 kW


Expert Solution