IBC Table 601 requires floor construction and associated secondary structural members in Types IV-A, IV-B, and IV-C construction to have a two-hour fire-resistance rating. Therefore, option B is correct.
This requirement applies to the complete floor assembly, not only the timber panel. The required two-hour performance may be established through the calculated fire resistance of the mass timber, the contribution of approved noncombustible protection, or a permitted combination of both. Any topping, protective membrane, connection protection, and edge condition that forms part of the approved rated design must be installed accordingly.
The ratings for other building elements should not be transferred to the floor. A three-hour rating applies to the primary structural frame and bearing walls of Type IV-A, but its floor construction remains two hours. Type IV-B and Type IV-C floors also require two hours, even though those construction types permit different degrees of exposed mass timber.
The special inspector must verify panel dimensions, approved layup, protection layers, joints, penetrations, connections, topping thickness, and other details that influence the floor’s rated performance.
References/Topics: 2021 IBC Sections 601 and 602.4; Table 601, floor construction and associated secondary structural members.
===============