A AWG THWN-2 PV output conductors from two PV arrays are run in the same 3 in, conduit to their respective functionally grounded inverters in the building. The three PV source circuits are each protected by a 15A fuse in the combiner box at the array. The conduit, which is strapped directly to the roof, is exposed to design temperatures of 140’ F (60’ C) during its 30 ft.
Exposed run. What is the MAXIMUM current carrying capability value of the PV output conductors?