NABCEP PV Installation Professional (PVIP) Board Certification PVIP Question # 7 Topic 1 Discussion

NABCEP PV Installation Professional (PVIP) Board Certification PVIP Question # 7 Topic 1 Discussion

PVIP Exam Topic 1 Question 7 Discussion:
Question #: 7
Topic #: 1

A 7KW/ 14 KWh multimode system has been installed at a residence, ac-couple with the customer’s existing 6.7kwh ac PV system. The system providers uninterrupted power to a protect loads subpanel, which is connected to a refrigerator,

Microwave, 1.0 ton are conditioner, three lightning circuit, and the 6.7kwac PV system. One month later, the homeowner moves additional circuits to the protected loads subpanel, substantially increasing the loads. Why would this cause, the backfed interconnection breaker in the main service panel to trip?


A.

The main service panel is no longer compliant with NCC 705.12.


B.

The load «the protected loads subpanel exceeds the PV system ac rating by 25%.


C.

The toad exceeds the capacity of the interconnection breaker.


D.

The total load exceeds the system's energy storage capacity of 14kWh.


Get Premium PVIP Questions