Wizard startup commissioning is designed to verify that the unit’skey controllable subsystemscan be started, regulated, and protected correctly. Conditions that prevent a subsystem from operating normally will directly cause commissioning failure. If thecondensate pump is stuck, the drainage function cannot be validated and water may accumulate in the drain pan, which is treated as a functional fault during commissioning. Ifindoor fan 2 drive is faulty, the fan system cannot meet airflow requirements or redundancy expectations, so the fan commissioning item fails. If theelectronic expansion valve (EEV) is not opened, refrigerant flow and cooling control cannot be established, so the cooling system commissioning fails because the unit cannot build a stable refrigeration cycle or reach expected operating parameters.
In contrast, thewater leakage ropeis aprotective detection accessoryused for leak sensing and alarming. While it is important for site safety and recommended for operation, its absence typically does not block the unit from completing the functional commissioning steps for fans, cooling, and drainage; it mainly affects leak detection coverage and related alarms rather than the basic startup commissioning pass/fail.