For the Huawei UPS5000-H, inverter startup is executed through theUPS’s own control interfaces, which provide the “Running Control / Inv. ON” operation with the required confirmations and permissions. TheUPS LCD (MDU touchscreen)supports inverter startup through menu operations such as selecting inverter start functions and confirming the action after authentication. TheUPS WebUIalso provides the same operational control path, where an operator logs in and issues theInv. ONcommand under the UPS monitoring/running control pages. These two interfaces are part of the UPS monitoring and control design and are explicitly used for commissioning and routine O&M actions.
By contrast,ECC(data center controller) andNetEco(management platform) are mainly used for site-level monitoring, alarm collection, visualization, reporting, and centralized management. While they can display UPS status and alarms (and may integrate with UPS data), inverter startup is defined as aUPS running control operationperformed on the UPS’s LCD or WebUI control plane to ensure proper authorization, safety checks, and command traceability.