APC Data Center University Associate Certification DU0-001 Question # 17 Topic 2 Discussion
DU0-001 Exam Topic 2 Question 17 Discussion:
Question #: 17
Topic #: 2
A UPS system consists of three modules in a parallel redundant configuration. Each module is rated to provide 200 kW of power. If the electrical load grows from 350 kW to 420 kW, what will happen?
A.
The UPS system will not provide any additional power beyond 400 kW.
B.
The UPS system will reach an overload state and switch to its static bypass.
C.
The UPS system's response will vary depending on the rate of electrical load growth.
D.
The UPS system will continue to support the load and become a capacity configuration.