CWBSP Exam Topic 1 Question 13 Discussion:
Question #: 13
Topic #: 1

What is the minimum calculated design area for a dry system protecting a light hazard attic space with a roof slope exceeding a rise of 2 units in a run of 12 units and a height at the peak of 10 ft (3 m) above the bottom of the truss using quick response sprinklers?


A.

1,521 ft2 (141.3 m2)


B.

1,170 ft2 (108.7 m2)


C.

1,950 ft2 (181.1 m2)


D.

2,535 ft2 (235.5 m2)