International Code Council Commercial Mechanical Inspector M2 Question # 2 Topic 1 Discussion
M2 Exam Topic 1 Question 2 Discussion:
Question #: 2
Topic #: 1
When a furnace is installed in a 66-inch-high attic, the maximum distance from the passageway access to the furnace shall be _____ ft., measured along the centerline of the passageway.
ICC mechanical access provisions for appliances in attics require the passageway to be not more than 20 feet in length , measured along the centerline of the passageway from the opening to the appliance, where the attic passageway is the standard reduced-height access condition. Since the attic height given is 66 inches, the standard maximum length applies, so Option C is correct. The 50-foot allowance applies only under a different exception where the passageway is unobstructed and at least 6 feet high for its entire length.