IBC Table 601, Footnote “a,” permits a one-hour reduction in the required fire-resistance rating of the primary structural frame and bearing walls where those elements support a roof only. Option C is therefore correct.
For Type IV-C construction, the normal Table 601 requirement for bearing walls is two hours. Where a bearing wall qualifies as supporting only roof construction, application of the footnote permits that rating to be reduced from two hours to one hour.
The limitation “supporting a roof only” is critical. The reduction cannot be applied simply because a wall is located at the uppermost occupied level. If the wall carries a floor, mezzanine, transfer load, occupied rooftop structure, or another structural element beyond qualifying roof construction, the condition for the reduction is not satisfied.
Options A and B are not reductions prescribed by Table 601. Option D would effectively eliminate the entire normal two-hour Type IV-C bearing-wall rating, which the footnote does not permit.
For inspection purposes, the approved construction documents and structural load path must substantiate use of the reduction. The fire-protection installation should then be checked against the actual reduced rating specifically authorized by the design.
References/Topics: 2021 IBC Table 601, Footnote “a”; Type IV-C bearing walls supporting roof construction only.
===============