The intended answer is ANSI/AWC NDS Chapter 16. The video option uses “AWS,” but the correct standards organization is the American Wood Council—AWC . Option D is therefore correct based on its intended reference.
IBC Section 722.1 expressly permits exposed wood members and wood decking to have their calculated fire resistance determined in accordance with Chapter 16 of the ANSI/AWC National Design Specification for Wood Construction. The method evaluates charring, the effective char depth, the reduced residual cross section, elevated-temperature effects, loading, and the remaining structural capacity for the required exposure period.
ACI 216.1 applies to concrete and masonry fire resistance. TMS 0216 addresses masonry assemblies. ASCE 29 Chapter 5 provides procedures for calculating the fire resistance of structural steel assemblies. Those references are code-recognized methods, but they apply to different construction materials.
For mass timber inspection, the approved calculations should identify the exposed surfaces, required rating, timber species or product, member dimensions, design loads, protective contribution, and connection treatment. Field reductions in member dimensions can invalidate the calculated fire resistance.
References/Topics: 2021 IBC Section 722.1; ANSI/AWC NDS Chapter 16; calculated fire resistance of exposed wood members and decking.
===============
Submit