Exact Extract — Huawei HCSA-Presales-Data Center Facility (Modular DC) V1.0 Training Material, PDF page 57
“FusionDC1000A 40ft Overview Item IT-N+X-380V IT-2N-380V-Tier III IT-2N-380V-(Non-Tier III) Total IT load ≤ 54kW Total IT load ≤ 54kW Total IT load ≤ 54kW Power density 6kW/R: 6pcs & 9kW/R: 2pcs 9kW/R: 6pcs 9kW/R: 6pcs Number of cabinets 8 6 6 Environment FusionDC1000A-40ft Appearance corrosion Class A/B/C environment (Class C is not supported at -40 ~ -20 ℃ ) requirements Cool type Row-level air cooling Anti-seismic GR-63-CORE Zone 3(the modular structure) Anti-wind Beaufort scale 12 (Wind speed ≤ 130km/h) Atmospheric Meets the 1440-hour salt spray test requirements corrositivity Module lifespan 25 years Module dimension 12192×2438×2896 (D×W×H, mm) FusionDC1000A-40ft Site Note: The basic concept of A/B/C environment is defined by GB/T15957 and Huawei enterprise standards. The corresponding ISO9223/12944 environments are classified”
Technical Deep Dive
FusionDC1000A IT-scenario configurations specify a total IT capacity of up to 54 kW. The 60 kVA specification applies to the UPS power capacity, not to the total IT load.
Both N+X and 2N versions of the 40-foot IT product support a maximum 54 kW IT load. The N+X model distributes capacity across six 6 kW racks and two 9 kW racks, yielding 54 kW in total. The 2N model uses six 9 kW racks, also yielding 54 kW. The 60 kVA UPS figure is an apparent-power capability and must not be confused with allowable IT power.
For this prefabricated 40-foot product, presales validation must distinguish physical cabinet arrangements, IT power density, UPS architecture, environmental limits, in-row cooling and the enclosure rating. A statement for one configured version must not be generalized to every deployment. Final designs also require suitable foundations, upstream connections, local safety compliance and commissioning checks.
Verification principle: confirm the exact product revision, operating condition, selected option and relevant Huawei documentation before using this result in a customer proposal. A feature shown for a particular configuration should not automatically be assumed to apply to every module or installation; normal technical, commercial and safety checks still apply.
Source reference: uploaded Huawei training material, PDF page 57.