Room temperature switches are used to detectfreezing conditionsin environments such as sprinkler valve rooms. An off-normal (supervisory) condition is triggered if the temperature dropsbelow 40 °F (4.4 °C).
NFPA 72 (2022), Section A.17.16.1.1:
“Low-temperature supervisory signals shall be initiated when the temperature falls below 40 °F (4.4 °C) unless otherwise specified.”
This signal helps prevent system damage or failure due to freezing.
Correct answer: B. 40 °F (4.4 °C)
===========