Household fire alarm systems have different performance requirements from commercial systems, but still must support essential alarm functions under loss of primary power.
NFPA 72 (2022), Section 29.10.5.1.1:
“The secondary power supply shall be capable of powering the system under quiescent load for 24 hours and then capable of operating the system during alarm for a period of 4 minutes (for general fire alarm) or 10 minutes (for household fire alarm systems).”
Correct answer: C. 24 hours in the normal condition followed by 10 minutes of alarm
===========