Testing of engine-driven generators is governed byNFPA 110, not NFPA 72. NFPA 72 references this standard for standby power systems.
NFPA 110 (2022), Section 8.4.1:
“Diesel generator sets shall be exercised at least once weekly.”
This includes running the generator under load and verifying automatic start capability.
NFPA 72 (2022), Section 10.6.3.2:
Refers to NFPA 110 for testing of standby/emergency power systems.
Correct answer: A. Weekly
===========