Option B is correct because the required protection time placed over a mass timber structural connection may be established through a code-recognized fire-resistance evaluation of that protective construction under standard fire exposure.
IBC Section 2304.10.1 regulates connections in Types IV-A, IV-B, and IV-C. The code allows connection fire performance to be demonstrated through testing where the connection is incorporated into the fire-resistance test or through an approved engineering analysis. AWC further clarifies that the protection applied over the connection must provide the necessary protection time and that its performance may be established using the methods recognized by IBC Section 703.3, including testing and engineering analysis based on ASTM E119 or UL 263 performance.
Option A is too narrow: testing an isolated fastener does not establish the fire protection of the entire connection. Options C and D also use the wrong temperature location. Where an engineering-analysis route is used, the temperature criterion applies to the connection itself , including connectors, fasteners, and portions of wood incorporated into the structural connection—not simply to the protected structural element or supported member.
References/Topics: 2021 IBC Section 2304.10.1; Section 703.3; AWC guidance on fire resistance of mass timber connections.
===============