Option A is the incorrect statement and therefore the required answer. Under 2021 IBC Table 601, an exterior bearing wall in Type IV-C construction requires a two-hour fire-resistance rating , not one hour.
The tall mass timber classifications progressively vary the degree of noncombustible protection and allowable exposure, but the structural fire-resistance requirements remain substantial. Type IV-A exterior bearing walls require three hours. Type IV-B exterior bearing walls require two hours. Type IV-C exterior bearing walls also require two hours. Thus, options B, C, and D correctly reproduce the Table 601 values.
The special inspector must also recognize that Table 601 is not necessarily the only rating criterion affecting an exterior wall. Exterior walls are additionally subject to the requirements associated with fire separation distance, particularly Table 705.5. Where another IBC provision requires a higher rating, that more restrictive condition controls.
For mass timber construction, compliance also depends on the prescribed protective system, member dimensions, connections, joints, intersections, and exterior-side protection. A wall cannot be accepted as compliant solely because the timber cross section appears substantial; it must conform to the approved rated design.
References/Topics: 2021 IBC Section 601; Table 601; Section 602.4; Table 705.5.
===============