Exact Extract — Huawei HCSA-Presales-Data Center Facility (Modular DC) V1.0 Training Material, PDF page 57
“Environment FusionDC1000A-40ft Appearance corrosion Class A/B/C environment (Class C is not supported at -40 ~ -20 ℃ ) requirements Cool type Row-level air cooling Anti-seismic GR-63-CORE Zone 3(the modular structure) Anti-wind Beaufort scale 12 (Wind speed ≤ 130km/h) Atmospheric Meets the 1440-hour salt spray test requirements corrositivity Module lifespan 25 years Module dimension 12192 × 2438 × 2896 (D × W × H, mm) FusionDC1000A-40ft Site Note: The basic concept of A/B/C environment is defined by GB/T15957 and Huawei enterprise standards. The corresponding ISO9223/12944 environments are classified into C1, (C2, C3), and C4. 57”
Technical Deep Dive
FusionDC1000A-40ft-IT operating specifications list either −40°C to +45°C or −20°C to +55°C, depending on configuration, with power derating typically above +45°C. Therefore, −40°C to +55°C is not a supported single operating range.
Neither environmental configuration spans minus 40 through plus 55 degrees Celsius. The designated low-temperature range extends to plus 45 degrees, while the high-temperature range begins at minus 20 degrees. Combining the low end of one envelope with the high end of another produces an unsupported claim. Cooling behavior, outdoor condenser performance and possible power derating make these limits important at presales design time.
For this prefabricated 40-foot product, presales validation must distinguish physical cabinet arrangements, IT power density, UPS architecture, environmental limits, in-row cooling and the enclosure rating. A statement for one configured version must not be generalized to every deployment. Final designs also require suitable foundations, upstream connections, local safety compliance and commissioning checks.
Verification principle: confirm the exact product revision, operating condition, selected option and relevant Huawei documentation before using this result in a customer proposal. A feature shown for a particular configuration should not automatically be assumed to apply to every module or installation; normal technical, commercial and safety checks still apply.
Source reference: uploaded Huawei training material, PDF page 57.